Ok glad you put the FV designation because there is Panel, Distribution, No.1 Mk 1 & also Box, Distribution, No.1 Mk 1.

 

The Box repairs are in EMER POWER P 164/1 (Part 1)

 

There is a circuit diagram on page 64 of this:

 

http://hmvf.co.uk/pdf/ALL%20CHARGED%20UP%204%20ver4-1.pdf

 

Bear in mind even when the circuit breakers are open there will still be through resistance of 165-191 ohms

 

Unlike a trip switch they need a sustained period of overload

30A breaker

35A for 15 mins

60A for 15-50 secs

100A for 4-6 secs

 

10A breaker

11A for 15 mins

20A for 10-25 secs